Did you have double circuits on the old panel that you reconnected the same way in the NEW 200-ampere Panel.
Sounds to me like you doubled up on the circuits on the same circuit breakers when you went to your NEW 200-Amp Panel.
This will cause the symtoms that you describe.
The wiring for each circuit should be on a separate circuit breaker.
Also, as Walks on Water's said, make sure that the size wire coming from the feeder is sized properly.
For 15-ampere loads the wire should be AWG No.14 copper.
For 20-ampere loads the wire should be AWG No.12 copper.
For 30-ampere loads the wire should be AWG No.10 copper.
Any load of 30-amperes or more should be a dedicated circuit for one individual type load. That is, like a Garbage Disposal, a Dryer, a Washer, a Range or an Air conditioner.
Electric Ranges, must be on a 50-ampere dual circuit breaker.
Most Electrical Dryers, must be on a 40-ampere dual circuit breaker.
Also, depending on what you went from to what you have now, i.e. the 200-ampere Panel, you must also increase the feeder wires coming from the Power pole all the way to the top of the Circuit Breaker Panel to AWG No. 3/0 copper. This is extremely importent.
If you only had a 100-ampere panel the largest the wire size would have been is AWG No.3.
If you only had a 60-ampere panel the largest the wire size would have been is AWG No.6.
Neither of these wire sizes are any where near large enough for the 200-ampere panel.
[This message was edited by donaldekliros on 06-19-02 at 10:30 AM.]
|
| |
| Posts: 696 | Location: St. Louis Missouri, USA | Registered: 06-03-02 |    |
|
Platinum Enthusiast
|
First, let me say that I am no electrician. I only know the bare minimum. (Not too bad at framing and finish, though.) So let me try to answer the questions you guys raised.
I don't believe the wire from the pole to the weather head was changed, but from the weather head to the box was upgraded.
I'm not sure what you mean by doubling up on the circuits. Several new circuits were added with lights and outlets separated, HVAC on a dedicated circuit, and heavy-draw appliances on dedicated circuits. Washer and dryer (gas) are on the same circuit as the outlets in the utility room. The utility room lights are the only ones that dim and they are on a circuit which includes the kitchen lights (4 75-watt bulbs), utility room lights (two 2x 75-watt fixtures), and exterior lights (4 150 watt fixtures and not often used).
I have no 30 amp 110 circuits and all wire was replaced with 12-2 except for the 220 circuits which is, of course, heavier.
Someone suggested that there may be something loose on the neutral bar, but I checked that and all is secure.
Remember, the only lights that are affected are those in the utility room.
What did I leave out?
|
| |
| Posts: 1799 | Location: Nashville, TN | Registered: 06-05-02 |    |
|
Gold Enthusiast

|
teeceeum: First off follow all of Don's excellent suggestions. In regards to you mentioning a possible break in the neutral, this would cause some definite and obvious symptoms. 1. Lights may dim way down as a load like the refrigrator comes on and never come back to full brilliance. or 2. Lights may flare brighter that normal as the 'fridg comes on. If either of these are what's occuring let us know, in the mean time do as Don advises and you should be fine. Regards Mike B. (AKA Byter)  [This message was edited by donaldekliros on 06-19-02 at 10:34 AM.]
|
| |