quote: Originally posted by frankvan: David, I don't know what kind of old dinosaur AC unit you had but assuming it was indeed a 40 amp circuit on 220 volts that is one heck of a big unit for a trailer. If the two breakers are adjacent in the load center their handles should be tied together for 220 volts and if they are individually rated at 20 amps they are still a 20 amp circuit, not 40 amp. If the wiring is #12, it is probably 20 amp. You should be able to replace the outlet with a single 120 volt receptacle and just not connect the red wire at either end, if you don't want to run a new cable. You would then be able to have another 120 volt 20 amp circuit for whatever purpose you choose to have one. Just make sure the 2 breakers are not tied together at the handles. The reason you have three wire cable is that the red and black are the two hot wires, the white is the neutral and the green or bare is the ground. Thatr would be typical for a 220/110 circuit where the compressor runs on 220 and the fan on 110 as is sometimes the case on some appliances. Hope that helps. P.S: just re-read your question. Please re-check those two breakers. If they are adjacent single pole breakers a jumper connecting them would be a short-circuit, not a doubling of capacity.
So what you are saing is tht I remove the connecting bar between the two 20 amp breakers. Rewire the line using the black, white and green (cutting off and capping the red wire at the breaker and the outlet) use only one of the 20 amp breakers - whire in a regular house outlet and I have regular current to draw from. Right? Actually I did take another look at the combined breakers, the wire goes to the source bar, not to the other breaker. Odd? Well the box was installed in 1960. The old AC unit did have to have a greater amperage for the compressor - and no, it wasn't a very powerful thing - just old tech - very old tech David
|
| |
| Posts: 3891 | Location: Leaving land, heading for the ocean | Registered: 06-03-02 |    |
|